shed supply

Guys,

Just some advice please! 

my son has installed a new 6m/m 3C SWA supply to his new wooden shed,( no extranous parts) its going to be terminated into a 4 way consumer unit (RCD main swt) and used to power & lighting in the shed and some lighting in the garden,

question is:

The source end in the house is a twin RCD board, so using a spare way on either side will give the supply cable RCD protection, but what about the RCD in the shed board? is it advisable to keep both? 



Parents
  • Thanks John and Alan,

    it confirms what I was thinking, just got to put it all together now?


    cheers guys