How a simple job can go wrong quickly....

Former Community Member
Former Community Member
Not my work before I relate:


Existing 3-ph circuit breaker DB in a shop has a 30 mA 4 pole RCD belatedly fitted in a separate enclosure to provide blanket RCD protection. OK, not ideal.

Electrician asked to install extra 13 A socket-outlet in window during shop hours so padlocks off the circuit's circuit-breaker and proceeds, He lets the circuit neutral and cpc touch when fitting the socket-outlet and out trips the RCD as expected. Resets and shop keeper then announces that the card reader, till, air-con and some lights not working.


All that equipment now duff (technical term!).


For an interesting weekend quiz, what happened?


Without hindsight and the work being done during opening hours, what would you have done differently?


Regards


BOD






Parents
  • A bit of insulation tape on the end of the neutral conductor as you dismantle the old fitting is a good start, maybe even a piano type Wago connector clipped onto it, also fold the CPC back when you are pulling the cable back out of a plastic enclosure.


    Regards the problem, were there still appliances connected to the circuit that was being worked on?


    Andy B.
Reply
  • A bit of insulation tape on the end of the neutral conductor as you dismantle the old fitting is a good start, maybe even a piano type Wago connector clipped onto it, also fold the CPC back when you are pulling the cable back out of a plastic enclosure.


    Regards the problem, were there still appliances connected to the circuit that was being worked on?


    Andy B.