perspicacious:
Not my work before I relate:
Existing 3-ph circuit breaker DB in a shop has a 30 mA 4 pole RCD
Mike has it. The neutral was disconnected before the phases when the R.C.D. tripped off and the loads were subjected to 400 Volts. Even though the loads would be connected like a star connected motor, the star point being at the neutral bar, the equipment could have been damaged by a transient over Voltage if the N. of the R.C.D. opened before the L1, L2 and L3 contacts.
Z.
perspicacious:
Not my work before I relate:
Existing 3-ph circuit breaker DB in a shop has a 30 mA 4 pole RCD
Mike has it. The neutral was disconnected before the phases when the R.C.D. tripped off and the loads were subjected to 400 Volts. Even though the loads would be connected like a star connected motor, the star point being at the neutral bar, the equipment could have been damaged by a transient over Voltage if the N. of the R.C.D. opened before the L1, L2 and L3 contacts.
Z.