I don't see the need to isolate the PE between the transformers and gear- I would earth them at both sources and the gear without hesitation.
ProMbrooke:
Ok- but what is the theory behind keeping a PE insulated? I know I keep asking because to be frank those behind BS7671 know WAAYYYY more than I do.
wallywombat:
Long bare cpc wires inside accessory and junction boxes have a habit of getting pushed against a line conductor or terminal when the box is pushed closed.
To ensure it is only earthed at one point - if it were bare (and buried) then it would effectively be multiple earthed
OMS:
ProMbrooke:
Ok- but what is the theory behind keeping a PE insulated? I know I keep asking because to be frank those behind BS7671 know WAAYYYY more than I do.
1 - To limit the impression of the HV side fault appearing on the LV Neutral - ie the Rise of Earth Potential transfer voltage
2 - To ensure it is only earthed at one point - if it were bare (and buried) then it would effectively be multiple earthed
Regards
OMS