"The tertiary power supplies considered are:
• batteries for UPS systems, inverter units and generators;
• HV/LV tripping/closing batteries;
• UPS systems;
• inverter units for central battery units and theatre operating lights "
ProMbrooke:
What about grouping of the automatic transfer switches? How do branches need to be subdivided or grouped?
I know I keep asking, but any example single lines? Or of Primary, Secondary and Territary?
Why is territary power needed if the medical equipment has backup batteries?
Excellent replies btw :)
OMS:
ProMbrooke:
What about grouping of the automatic transfer switches? How do branches need to be subdivided or grouped?
I know I keep asking, but any example single lines? Or of Primary, Secondary and Territary?
Why is territary power needed if the medical equipment has backup batteries?
Excellent replies btw :)
There are "typical" UK biased SLD's in HTM 06-01 - take a look, but note they are very high level to demonstrate the type of load supplied from the type of system
Even if a particular piece of kit (BiPap pump as an example) has integral batteries, you probably want to save those until it's last ditch and you are moving the patient - until you reach that point, the healthcare environment needs to provide the support - hence the tertiary systems that will ride you through engagement with your secondary power systems (many clinical applications have defined allowable break times)
As I said, read HTM 06-01 first, that should give you a good understanding.
Is this just curiosity, or are you planning on embarking on a design ?
Regards
OMS