How is a hospital power system typical designed in the UK, Europe and Russia? Does anyone have a single line diagram?
    Maybe this will work...
    attachments.zip
  • Very interesting, and not quite the same philosophy - in the event of failure of external power it makes perfect sense to cluster those loads you wish to maintain, and those you will drop, but I might have expected things like ventilation and maybe lights to be a mix of maintained and not, to reduce the load on the genset, but maintain a tolerable if not ideal environment inside.
    The thinking for preventing large area loss due to a single fault in the building is not really quite the same over here either - if one of the critical group sub-mains gets spiked, or even if it just needs to be dead tested as part of a periodic inspection,  it is not clear how you keep everything else working, I presume there are other links not shown, or the final circuit sub-division is such that very small areas can be isolated quickly.
  • ProMbrooke:
    That all looked a bit muddled.
    I think that you need to know how a hospital works - clearly OMS does!
    I fear that the use of electrocautery has led to a generation of surgeons who are not used to tying sutures (seriously!) but a lot of surgery can be done without electricity (battery head lights are useful, but they don't count) so oddly, in most cases, the operating theatre doesn't have to be no. 1 priority. Anaesthetists don't need leccy either - Triservice apparatus.
    Chris Pearson:
    ProMbrooke:
    What is muddled? Don't seek blame in me, seek it in the NFPA. Battery operated lighting in ORs is recommended by NFPA99 but not required. Most hospitals in the US are wired this way.
    mapj1:
    Hence my curiosity- the differences are vast and also behind my "slow" grasp.
    Lights are often a mix, but don't have to be if just following code in its literal interpretation. Just that a certain amount of receptacles are on normal power. The boxes are panelboards or MCCs- there are no links beyond them. If a critical branch goes down all life support equipment gets plugged into the white outlets in the OR, ICU or critical care area. Here is a typical example, 2/3 red outlets on critical, 1/3 on normal power:
    attachments.zip
    OK - what you call the headwall is typically described in UK parlance as the bed head, and is covered in HTM 08-03 - Bedhead Services
    For each of your examples, I could map the medical gas outlets, earthing  points, lighting control, patient entertainment control, exam lamp and critical and normal sockets to a virtually identical set up in a UK or European Hospital
    I mentioned the AIA Healthcare guides and the links to relevant NFPA and NEC Codes - and therein is the principal difference. Your USA experience will be based on a "by the code" approach - code says, you do. In the UK and Europe, we achieve much the same things but we use a much more pragmatic approach based on clinical risk assessment. We don't generally mandate number of branches, feeders, ATS etc - we just state the performance requirements (again, read HTM 06-01). From there we have a process of competent designers interpreting requirements objectives for a specific site based on particular assessment of clinical risk.
    If we took a typical 500 bed acute hospital in the USA and in the UK, you would be surprised actually how similar the systems are - we just get there in a different way, which is generally quite normal based on the different approaches on either side of the Atlantic to many engineering challenges. Essentially, you guys rely on the "Code" - if the code says do it, you do it - we Brits however are more likely to adopt the approach of "Code is for the guidance of wise men, and the adherence of fools" - don't take that personally, it's just how we used to describe some of our American colleagues.
    OMS
    Chris Pearson:
    ProMbrooke:
    Sure Chris - a good gasser and slasher team and a handful of switched on nurses can keep pretty well anyone alive under pretty dire or grim conditions  - electricity is often of minor importance.
    Of course, we don't want to stress out the surgical or ITU teams unnecessarily as part of the day job, so the engineering systems give them a fur lined environment to work in - I guess a few get a bit too fond of "fur lined" and forget what the real sharp end might look like, and what actually can be achieved.
    That said, most of the lads and lasses I used to come across are pretty capable of working under the most appalling conditions if they actually have to - I guess that's attitude of mid rather than technical ability though.
    I've never had to reach in and grip someone's heart and keep squeezing  - so I've no idea how I'd hold up TBH
    OMS
    With a hospital you are looking to keep the power going for as long as possible and ensure that there is duplicity in the critical areas so that a supply can be pretty much depended upon, actually its the post op care areas and the ICU that really need the power as these areas that individual is not being baby sat like they are in the theatre. if the power goes down you better hope that there is back up on the equipment just to ride through until the staff can get a grasp on all thats going on.
    So in a hospital you have an electrical supply, this supply is backed up by a generator or generators depending on the site load requirements. Also if you are applying n+1 then this has to be considered with the generators.
    So this supply is provided to the hospital - you have the risk when the supply fails of a delay in power till the generators kick in so you cover that with a UPS to provide fill in between utility and generator.
    So this UPS back up is used to supply all the critical equipment on site. You will have a UPS system installed that can cover the electrical system and ensure that there is no risk from a single point of failure. Generally you would specify two UPS systems on an n+1 layout so that if one UPS fails the other can keep the system going. This would be kept seperate and the wiring seperated as well to ensure that a source of power is available to the protected equipment. The biggest fear being a single point of failure affecting the critical areas.
    An additional type of supply is provided to a hospital which is an isolated power supply This is a supp,y that is un referenced to earth. This means that the wiring or equipment could have an insulation failure but it will allow that item to keep going and would alarm to let the staff know to take action. it provides a further degree of protection. In addition to that there would be interweaving of the supplies in and around these critical areas to ensure that in the vent of a loss of one supply it would not affect the other supply.
    simple really and all about ensuring that the patient electrical supplies are kept well protected.
  • OMS:
    Last resort! But I have it on good authority that it has been done successfully in the back of a Chinook flying somewhere over Afghanistan.
    OMS:
    OMS
    Not personal at all, but 100% correct and spot on! ?
    If you ask me, I like your approach better in that we don't typically see UPS tertiary power in critical care areas. I like the fact UK code lets you choose how to sub-divide the branch circuits and how many ATSs to use. Also it seems like UK hospitals end up with two sources of backed up power in each critical care location instead of one normal and one emergency as typical in the US.
    If you don't mind I will read more of HTM 06-01 and ask questions. Forgive me if they are elementary or seem argumentative. I have zero experience or knowledge involving UK backup and critical power systems. I am learning this for the first time.