mapj1:
Very interesting, and not quite the same philosophy - in the event of failure of external power it makes perfect sense to cluster those loads you wish to maintain, and those you will drop, but I might have expected things like ventilation and maybe lights to be a mix of maintained and not, to reduce the load on the genset, but maintain a tolerable if not ideal environment inside.
The thinking for preventing large area loss due to a single fault in the building is not really quite the same over here either - if one of the critical group sub-mains gets spiked, or even if it just needs to be dead tested as part of a periodic inspection, it is not clear how you keep everything else working, I presume there are other links not shown, or the final circuit sub-division is such that very small areas can be isolated quickly.
mapj1:
Very interesting, and not quite the same philosophy - in the event of failure of external power it makes perfect sense to cluster those loads you wish to maintain, and those you will drop, but I might have expected things like ventilation and maybe lights to be a mix of maintained and not, to reduce the load on the genset, but maintain a tolerable if not ideal environment inside.
The thinking for preventing large area loss due to a single fault in the building is not really quite the same over here either - if one of the critical group sub-mains gets spiked, or even if it just needs to be dead tested as part of a periodic inspection, it is not clear how you keep everything else working, I presume there are other links not shown, or the final circuit sub-division is such that very small areas can be isolated quickly.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site