Supplementary CPC/SWA Resistance Ratio

Evening all, as the title above i am just trying to get my head around how a supplementary CPC will help lower the Zs to achieve a sufficent 5s disconnection time. My thinking is that the SWA and CPC are supplementary mechanically connected at both earth bars (supply and load) so the fault current will divide based on the resistance ratio (even if it takes the longer route through the supplementary CPC if there was a fault on the amour to line conductor).

 

I have attached a sketch of this for clarity. 


I also know strapping a cpc on the side of the armour is bad practise, however im just trying to get my head around the principles.
Parents
  • Strictly speaking it is not good science to directly add resistances to impedances. It would be better to say Zs = Ze+Z1 +Z2. In addition fault current flowing in the SWA armour may have a choking effect on the current flowing in the external CPC. To be safe and have a margin of comfort have a full size additional CPC to achieve your desired Zs.
Reply
  • Strictly speaking it is not good science to directly add resistances to impedances. It would be better to say Zs = Ze+Z1 +Z2. In addition fault current flowing in the SWA armour may have a choking effect on the current flowing in the external CPC. To be safe and have a margin of comfort have a full size additional CPC to achieve your desired Zs.