Alasdair Anderson:
John Peckham:
`You cannot apply diversity to a single piece of equipment for sizing circuit protection and cable sizing. Diversity can be applied to individual items of equipment when considering the maximum load on a distribution circuit or an installation.
The cable and the circuit protection should be rated for the "Plated" load or the manufacturers instructions.This gives rise to a bit of an anomaly....
If I have a cooker with a 7.5kW four plate hob and a 3kW double oven/grill I can't apply diversity.
If I have a fitted kitchen with a built-in 3kW double oven/grill and a separate 7.5kW four plate hob then I can apply diversity.
They surely can't both be right.
John Peckham:
`You cannot apply diversity to a single piece of equipment for sizing circuit protection and cable sizing. Diversity can be applied to individual items of equipment when considering the maximum load on a distribution circuit or an installation.
The cable and the circuit protection should be rated for the "Plated" load or the manufacturers instructions.
AJJewsbury:
You cannot apply diversity to a single piece of equipment for sizing circuit protection and cable sizing. Diversity can be applied to individual items of equipment when considering the maximum load on a distribution circuit or an installation.
Where on earth did you dig up that quote from? AFAIK that kind of thinking was dropped from the regulations decades ago - about the time we started using 13A sockets - and cooker diversity was well established even before that.
You cannot apply diversity to a single piece of equipment for sizing circuit protection and cable sizing. Diversity can be applied to individual items of equipment when considering the maximum load on a distribution circuit or an installation.
perspicacious:
Who said anything about fault conditions?
Ah, I was quoting out of the 17th: 433.1 "Every circuit shall be designed so that a small overload of long duration is unlikely to occur." and earlier editions echo the same.
My 18th isn't to hand so apologies if I've got the wrong Reg no.
perspicacious:
And conversely, when I was doing a lot of pub PIRs (as they were at the time), it was quite usual to find an innocent looking twin basket deep fat fryer with two 13 A plugs prefitted when it was actually one appliance. The landlord saw nothing wrong with plugging it into the nearest double socket with the consequence of there being less than 3 kW left on the rfc in a very busy kitchen........
perspicacious:
Is that the long and short of it Chris?
How long is the turkey in the oven for?!!!!!
Regards
BOD
PS check your PM.........!