Cable specification for Fire/BMS installation on a large complex site

Hi all

Does any one have a steer on the above? Perhaps any one in the consulting side of things?


Colin  MIET
Parents
  • Former Community Member
    0 Former Community Member
    OK - well the fire detection and alarm system needs separate containment - and as a quick answer, if you have phased or staged evacuation or anything that looks like a stay put procedure for selected key personnel then you will need an enhanced grade as defined in BS 5839-1 (it will refer you to allowable cable standards). Ditto if you need to send signals to any adjacent or adjoining facilities and/or if there are fire and smoke dampers in place that you need to control


    Regards


    OMS
Reply
  • Former Community Member
    0 Former Community Member
    OK - well the fire detection and alarm system needs separate containment - and as a quick answer, if you have phased or staged evacuation or anything that looks like a stay put procedure for selected key personnel then you will need an enhanced grade as defined in BS 5839-1 (it will refer you to allowable cable standards). Ditto if you need to send signals to any adjacent or adjoining facilities and/or if there are fire and smoke dampers in place that you need to control