2. In the CoP for EV Charging Equipment Installations 3rd Ed., Figure 5.3. it shows the CP for the EV charge point originating from the N between the transformer and the RCD for the chargepoint. Doesn't this contradict 722.312.2.1 in BS7671, as its effectively a PEN conductor at that point? Or does 722.413 override this?
Naj93:
I hear that a manufacturer has now made an EV charger that can be installed to PME systems. (myenergi - zappi - other manufactures may manufacture something as well). I've not installed one of these, but they say it's compliant with the reg 722.411.4.1 (iii)
Might be worth a look.
mapj1:
It may be that by the time you need to install this, you will be allowed to use the PME earth providing you can supply the charger via a contactor that disconnects all conductors, including the CPC, if the line voltages go out of spec enough to indicate a supply side fault.
If you look at the post this morning about the new draft COP for charging and follow the link - you do have to give a name and address and an Email, but as far as I can tell they are not checked, then you can view the COP in a sub window, and even save a copy to view locally (though the watermarkings ask you not to) Anyway, this allows the use of an "Open PEN detector" and refers to an yet to be included section 722.411.4.1 (iv) in the regs, and then describes a voltage operated device for installations with single-phase supplies, that operates when the line to neutral voltage at the charging point is outside a specified range.
For 3 phases, the voltage between the phase centre and a reference electrode can be used, again to fire an all-pole LLLNE trip.
This is a change that will I think make charging possible in cases like that you describe.
Anyway, this allows the use of an "Open PEN detector" and refers to an yet to be included section 722.411.4.1 (iv) in the regs, and then describes a voltage operated device for installations with single-phase supplies, that operates when the line to neutral voltage at the charging point is outside a specified range.
If my O-level maths and back of an envelope phasor diagrams are anything like right, I think it's possible (with the wrong combination of loads on the various phases) to have the severed PEN hovering at more than 100V above Earth, but still have a nominal 230V L-N at the charge point.
AJJewsbury:
One other thought (sorry, going off at a tangent now) ... should these devices be subject to any testing? (either on testing or during periodics). I guess they'd share some basic technology with RCDs (current/voltage sensing, comparison with a threshold and triggering mechanical contacts) - and if after all these years RCDs are considered vulnerable to failure should we not take similar precautions with these new devices?
I guess a variac and a stopwatch would do - but maybe there's a market for a new kind of tester...