mapj1:
It may be that by the time you need to install this, you will be allowed to use the PME earth providing you can supply the charger via a contactor that disconnects all conductors, including the CPC, if the line voltages go out of spec enough to indicate a supply side fault.
If you look at the post this morning about the new draft COP for charging and follow the link - you do have to give a name and address and an Email, but as far as I can tell they are not checked, then you can view the COP in a sub window, and even save a copy to view locally (though the watermarkings ask you not to) Anyway, this allows the use of an "Open PEN detector" and refers to an yet to be included section 722.411.4.1 (iv) in the regs, and then describes a voltage operated device for installations with single-phase supplies, that operates when the line to neutral voltage at the charging point is outside a specified range.
For 3 phases, the voltage between the phase centre and a reference electrode can be used, again to fire an all-pole LLLNE trip.
This is a change that will I think make charging possible in cases like that you describe.
mapj1:
It may be that by the time you need to install this, you will be allowed to use the PME earth providing you can supply the charger via a contactor that disconnects all conductors, including the CPC, if the line voltages go out of spec enough to indicate a supply side fault.
If you look at the post this morning about the new draft COP for charging and follow the link - you do have to give a name and address and an Email, but as far as I can tell they are not checked, then you can view the COP in a sub window, and even save a copy to view locally (though the watermarkings ask you not to) Anyway, this allows the use of an "Open PEN detector" and refers to an yet to be included section 722.411.4.1 (iv) in the regs, and then describes a voltage operated device for installations with single-phase supplies, that operates when the line to neutral voltage at the charging point is outside a specified range.
For 3 phases, the voltage between the phase centre and a reference electrode can be used, again to fire an all-pole LLLNE trip.
This is a change that will I think make charging possible in cases like that you describe.