However, there are still many installations where the three conditions (for omission) are not met; usually a lack of RCDs.
wallywombat:
Before we get too hung up about existing installations, let's consider just a new build to 18th Ed. Is there a scenario which is fully 18th compliant and which requires supp bonding?
wallywombat:
I don't follow. 701.411.3.3 requires RCD protection for the circuits in the bathroom. Then 701.415.2 (v) says that you can omit bonding if (amongst other things) RCDs are present. Or are you saying that for existing installations which don't have an RCD on the relevant circuits, then its ok to modify the circuit without adding an RCD, but you must add supplementary bonding???
The effectiveness of the connection of extraneous-conductive-parts in the location to the main earthing terminal may
be assessed, where necessary, by the appication of Regulation 415.2.2.
and then
415.2.2 The resistance R between simultaneously accessible exposed-conductive-parts and extraneous conductive parts shall fulfil the following condition:
R <50 V/Ia in AC systems... where Ia is the operating current in amperes (A) of the protective device or:
(i) for RCDs, Ian
(ii) for overcurrent devices, the 5 s operating current.
Not unknown for items like a cast iron soil stack, or existing metal radiators, to be not really as well bonded back to the MET as this requires, and at the same time not well enough isolated from ground to be truly considered not to be an extraneous part.
In such a case a local bond solves the issue.
Water and gas pipes etc should already be main bonded if they introduce a potential.