Can this device be installed in an installation and comply with B.S. 7671?

Can this gadget be B.S. 7671 compliant?

https://www.tdk-electronics.tdk.com/en/2487672/products/product-catalog/emc-components/leaxield?wt_mc=gaw_LeaXieldEnglish_rccb&gclid=EAIaIQobChMI8vfs-tTi5gIVFODtCh0I3gl5EAMYASAAEgL6uvD_BwE


More about it.....

https://www.youtube.com/watch?v=42g6Mawr3s4




Z.
Parents

  • I was also thinking of a reg that prohibited introducing voltages(?) to an RCD other than those required for periodic testing by an approved testing device, but cant find it



    I suspect you're thinking of 531.3.1.202 - but the wording is rather too specific - "It is not permissible to introduce an external connection for the purpose of intentionally creating a residual current to trip an RCD."


      - Andy.
Reply

  • I was also thinking of a reg that prohibited introducing voltages(?) to an RCD other than those required for periodic testing by an approved testing device, but cant find it



    I suspect you're thinking of 531.3.1.202 - but the wording is rather too specific - "It is not permissible to introduce an external connection for the purpose of intentionally creating a residual current to trip an RCD."


      - Andy.