alex.white:
For what does PELV require protective conductor? And also what is differences between PELV and FELV? Both of them require PE conductor
For what does PELV require protective conductor? And also what is differences between PELV and FELV? Both of them require PE conductor
FELV on the other hand permits only simple separation - e.g. the equivalent of just single insulation between primary and secondary windings - so a single fault could impose mains voltage on the ELV circuit.
Not even that , a FELV may be designed to not any isolation at all between the LV and ELV, in normal operation. The example of the ELV signal relative to neutral that between the linked kidde smoke alarms, is also an example of FELV. So the cable of the ELV link needs the same insulation and respect as the L and N.
I'm not sure a PELV circuit requires a protective conductor at all - it may have one if you want (e.g. for functional reasons), but as far as I can see it's not actually required by regs.
PELV circuits (unlike SELV ones) may be connected to Earth - but that connection need not involve a protective earth conductor - as it's not required for protection against electric shock as far as the PELV circuit is concerned.
Any old means of earthing, or just a potential for fortuitous contact with earth (say lack of insulation on one pole in an earthy environment), would be enough to make a circuit PELV rather than SELV.
mapj1:
SELV is the double insulated version of ELV and is 2 faults to danger by insulation at the supply end.
PELV has a CPC for 2 reasons.
firstly, for the same reason that the mains does - to provide prompt disconnection of faults from the 'live' side to ground that might otherwise go un-noticed, and
secondly to prevent a failure of the power supply that generates the extra low voltage from the mains, from impressing the mains voltage on the output and not being noticed. Imagine a transformer with a short at one point part way up the primary and part way the secondary.. This allows a single insulated power supply construction.
FELV a catch all for any ELV kit that is not really PELV or SELV, including designs where there is no isolation between the LV and ELV parts of the circuit. Therefore the protection requirements for the higher voltage have to be applied to the entire circuit.
Examples include LED lights with a resisitive or capacitive dropper from mains to 12V or whatever the LED needs, and the internals of things like PIRs and some linked smoke alarms where the internals are at 9V or 12V, but use the neutral as a common reference and so the ELV parts are not isolated from the mains.
alex.white:
mapj1:
SELV is the double insulated version of ELV and is 2 faults to danger by insulation at the supply end.
PELV has a CPC for 2 reasons.
firstly, for the same reason that the mains does - to provide prompt disconnection of faults from the 'live' side to ground that might otherwise go un-noticed, and
secondly to prevent a failure of the power supply that generates the extra low voltage from the mains, from impressing the mains voltage on the output and not being noticed. Imagine a transformer with a short at one point part way up the primary and part way the secondary.. This allows a single insulated power supply construction.
FELV a catch all for any ELV kit that is not really PELV or SELV, including designs where there is no isolation between the LV and ELV parts of the circuit. Therefore the protection requirements for the higher voltage have to be applied to the entire circuit.
Examples include LED lights with a resisitive or capacitive dropper from mains to 12V or whatever the LED needs, and the internals of things like PIRs and some linked smoke alarms where the internals are at 9V or 12V, but use the neutral as a common reference and so the ELV parts are not isolated from the mains.
So many thanks for replying. Please help me also to know about these questions:
1- you said for PELV "to provide prompt disconnection of faults from the 'live' side to ground that might otherwise go un-noticed" and "to prevent a failure of the power supply that generates the extra low voltage from the mains, from impressing the mains voltage on the output and not being noticed". These could happen for SELV, but it have no CPC. In SELV why we have not any concern about un-noticed? Because of double insulated in SELV?
2- Is double insulated, requirement for SELV?
3- Please give me some practical application example for PELV. (For SELV I know: ZONE 0 of bathroom and for FELV you gave LED lights example).