For what does PELV require protective conductor? And also what is differences between PELV and FELV?

Former Community Member
Former Community Member
For what does PELV require protective conductor? And also what is differences between PELV and FELV? Both of them require PE conductor


Parents
  • PELV may also have earthing for functional reasons, i.e. the protective conductor is a combined protective and functional earthing conductor. This may be, for example, for electromagnetic compatibility, measurement purposes, or discharge of static electricity.


    BUT - that does not make it FELV.
Reply
  • PELV may also have earthing for functional reasons, i.e. the protective conductor is a combined protective and functional earthing conductor. This may be, for example, for electromagnetic compatibility, measurement purposes, or discharge of static electricity.


    BUT - that does not make it FELV.