Tingles from lead flashing on house with solar array - anyone else seen this?

A long phone call today with a good friend who is a Niciec Contractor, who is now facing a rather odd problem with a domestic solar array installed by others. The DC string cables from the panels on the roof to the inverter run along some distance under lead flashing, and now workers on the roof are reporting tingles from the metal flashing when standing on their scaffolding.

As part of the testing , the cables have been checked and are isolated from the metal and not damaged in any way. There is a rather variable AC voltage on the lead, relative to the scaffolding, which is at more or less the same as local earth potential. The measured voltage is considerably more when the inverter is on though does not fall completely to zero when it is not.

Now I have not seen the set up, as it is many miles away, but as the voltage is so variable depending on conditions, I am minded to suggest it is capacitive coupling between the DC string cables and the adjacent metal.

I'm also going to suggest earthing the flashing in any case.

However, has anyone else with more experience of modern domestic solar installation ever seen this sort of thing?

 And am I even right in assuming the inverter  action means DC strings are commutating at 50Hz relative to the mains, as would be needed to explain this effect?

Or am I going up the wrong tree altogether ?


The inverter suppliers are not much help, being more of a kit supplier than technical experts on what they stock, and this is not in their FAQ.

Parents
  • That is a good point, though no known HV lines in this case. I suppose rubber pads and non-skid feet, and the tendency to use shims of wood to make up levels mean that scaffolding may often be electrically floating and free to pick up an arbitrary voltage. In this specific case the metal scaff has been checked and  is at or very near terra-firma earth voltage, but experience on other sites may explain the scaffolder's apparently rather "gung-ho" attitude.


    round here these things
    fcd4fb23664f54a123c8deff56569bd6-huge-scaff_foot.jpg


    and the big screw up jacklegs seem pretty common, and I'd expect that arrangement to be pretty insulating. I;d be rather less sure of the C to ground, perhaps I need to sneak out and measure one when it is not raining
Reply
  • That is a good point, though no known HV lines in this case. I suppose rubber pads and non-skid feet, and the tendency to use shims of wood to make up levels mean that scaffolding may often be electrically floating and free to pick up an arbitrary voltage. In this specific case the metal scaff has been checked and  is at or very near terra-firma earth voltage, but experience on other sites may explain the scaffolder's apparently rather "gung-ho" attitude.


    round here these things
    fcd4fb23664f54a123c8deff56569bd6-huge-scaff_foot.jpg


    and the big screw up jacklegs seem pretty common, and I'd expect that arrangement to be pretty insulating. I;d be rather less sure of the C to ground, perhaps I need to sneak out and measure one when it is not raining