AJJewsbury:
If any wadding is to be put into the wall, then we potentially end up with Reference Method A, in which case the 2.5 mm2 cable is downgraded to 20 A.
So what's the problem? - since the regs changed a few(*) years back so that we only need to meet a 20A requirement for ring cables, rather than 0.67x In, can't you have a compliant installation even with thermal insulation within the stud walls?
AJJewsbury:
If any wadding is to be put into the wall, then we potentially end up with Reference Method A, in which case the 2.5 mm2 cable is downgraded to 20 A.
So what's the problem? - since the regs changed a few(*) years back so that we only need to meet a 20A requirement for ring cables, rather than 0.67x In, can't you have a compliant installation even with thermal insulation within the stud walls?