Social Housing EICR Contract

Former Community Member
Former Community Member
OK. Id be very grateful for some experienced testers opinions regarding how they would proceed if they were in my shoes.


I accepted a contract carrying out EICR's for a social housing contract.


Now, I havent been doing EICR's since 2015. Back then I would charge a day rate and test every circuit 100%.


Probably the biggest part of how I used to do things was disconnecting every last piece of current using equipment and doing I.R between neutral and line, line and earth and neutral and earth. It used to take a lot of effort to find every piece of equipment and often things were found which the customer, despite living in the property all their lives didnt know existed.


Here I have 1.5 hours per property, we arent allowed to leave FI, C1 or C2 problems (withing reson of course but generally theres a lot to sort out)


1st question - If your R1 + R2 value is lower than either your RN or your R1 continuity tests - What would that tell you and what would you do to prove the circuit is ok for continued use in its current state?


2nd question - If you had either excessively high, or no continuity on R1, RN or R2 end to end readings, how can you quickly and simply prove the circuit is stilll safe for use without getting deep in to further investigation?


3th question - When doing an I.R test whereby........ line+neutral are connected together and tested to earth - Is there any electronic or electrical device which, if connected, could result in a test failing the circuit? I had one today 0.79 ohms


Parents
  • I work in Social Housing now.

    Almost all of our properties, electrically, are in near perfect condition. 

    It is only due to the Tenant breaking things that I give a C1/ C2.


    It seems like you have signed up to a very poor Contract for you. Why did you agree to such terms?

    It generally takes 30-45 minutes for me to write up the report.

    I&T can be done in 1.5 hours. I've got it down to a pretty quick job, even 30 mins in some properties.

    Firstly go in, check bonding and incomers. Turn all circuits off, test the Ze, global insulation, Ring end to ends,Ring R1+R2, RCD tests.

    I can then energise again, and go round doing the R2's with a wander lead. Then Zs. I know that isnt perfect, but, it gets the power on quick for moaning tenants.


    If you are doing repairs too, then you really need 3 hours per house. I did one a few weeks ago that needed 12 hours of repairs.
Reply
  • I work in Social Housing now.

    Almost all of our properties, electrically, are in near perfect condition. 

    It is only due to the Tenant breaking things that I give a C1/ C2.


    It seems like you have signed up to a very poor Contract for you. Why did you agree to such terms?

    It generally takes 30-45 minutes for me to write up the report.

    I&T can be done in 1.5 hours. I've got it down to a pretty quick job, even 30 mins in some properties.

    Firstly go in, check bonding and incomers. Turn all circuits off, test the Ze, global insulation, Ring end to ends,Ring R1+R2, RCD tests.

    I can then energise again, and go round doing the R2's with a wander lead. Then Zs. I know that isnt perfect, but, it gets the power on quick for moaning tenants.


    If you are doing repairs too, then you really need 3 hours per house. I did one a few weeks ago that needed 12 hours of repairs.