The maximum permissible disconnection time is 0.4 s in TN system. Why and from where this value (0.4 s) is obtained?

Former Community Member
Former Community Member
The maximum permissible disconnection time in in the event of a short circuit between a phase conductor and a body or protective conductor or a protective-neutral conductor is 0.4 s in TN system. Does anybody know this value (0.4 s) obtains from where? How this value is obtained?
  • As I understand it, the 0.4s disconnection time was an outcome of a working group within IEC that set about developing a maximum touch voltage curve for use in installation design so that maximum disconnection times could be set. That curve itself was derived from a line plotted in the AC-3 zone of the graph AJ posted above (the body time/current curves) and certain other assumptions. Amongst the important assumptions made was the stipulation that the curve was relevant for normal dry conditions. Since we all have different body impedance it was decided that the body impedance would be representative of a value hand to foot exceeded by 95% of the population. That value is 1000ohms. To allow for two hand contact to two feet the value was reduced by half to 500 ohms. A value of 1000 ohms was then added back in to account for footwear and floor resistance. Body impedance is affected by many things including the value of voltage. So for example, for the same person at 50vAC the total assumed impedance is  taken as 1725 ohms while at 220VAC it is taken as 1500 ohms. 

    So the same person making two hand to two feet contact at 50v would suffer a body current of 50/1725 = 29mA and at 220v it would be 220/1500 = 147mA. Reference to the line established on the body time/current current as noted above, the latter would require disconnection within 180ms whilst there is no limit on the former. 

    Similarly, at 100VAC, the body impedance is indicated as 1600 ohms which would result in a body current of 62mA and a required disconnection time of 400ms. This value of touch voltage Is taken to be a likely magnitude touch voltage that would exist where the nominal voltage is 230v but assumes that the relationship between R1 and R2 is equal in terms of resistance. This is not the case in the UK where reduced csa is used for twin and earth cables which, when using the same calculator for prospective fault voltage, would result in higher values and, in consequence, shorter required  disconnection times. It would paper that we are happy to stick with the 0.4s anyway.

  • but assumes that the relationship between R1 and R2 is equal in terms of resistance. This is not the case in the UK where reduced csa is used for twin and earth cables which, when using the same calculator for prospective fault voltage, would result in higher values and, in consequence, shorter required  disconnection times.



    But to some extent our use of reduced c.p.c.s is mitigated by main bonding - as the shock (inside a building) is likely to be, not to true earth, but to an earthed piece of metalwork (exposed- or extraneous-conductive-part) that's connected to the MET. The touch voltage is then reduced, as the victim is only exposed to the v.d. across R2 within the installation - and is spared the corresponding v.d. along the DNO's PE or PEN.  There can't be solid guarantees of course as there are many variables that are out of our control - but reasonable assumptions tend to suggest that often bonding will balance out the effects of reduced c.p.c.s.


      - Andy.
  • Andy,

    Protective bonding is accounted for in the calculation for touch voltage. I agree that there are variables and perhaps some arbitrary assumptions. The touch voltage used in the calculation is taken from;

    Ut = mxcxU /m+1

    Where Ut is the prospective touch voltage, m is the ratio of protective conductor resistance to phase conductor resistance m=R2/R1, c is similarly the relationship between the internal impedance and overall impedance c= R1+R2/Zs (taken as an arbitrary 0.8), U is 1.1 x Uo


    I should say, by the way, all this is taken from the Commentary on the 16th Edition by the excellent Mr Paul Cook.
  • Former Community Member
    0 Former Community Member
    Or simply use:


    Vtouch = Ifault x R2


    Where R2 is the resistance of the CPC within the installation, if the installation is bonded  - and is the whole resistance of the earth path if not bonded


    That should illuminate admirably why bonding in a TT system is a jolly good idea


    Regards


    OMS

  • OMS:

    Or simply use:


    Vtouch = Ifault x R2


    Where R2 is the resistance of the CPC within the installation, if the installation is bonded  - and is the whole resistance of the earth path if not bonded


    That should illuminate admirably why bonding in a TT system is a jolly good idea


    Regards


    OMS




    That's true of course but the OP wanted to know the origin of the 0.4s disconnection time. It probably also explains the 0.2s specified for the TT system. What remains for us to establish the is the origin of the 5s and 1s disconnection times.

  • Former Community Member
    0 Former Community Member

    lyledunn:

     



    That's true of course but the OP wanted to know the origin of the 0.4s disconnection time. It probably also explains the 0.2s specified for the TT system. What remains for us to establish the is the origin of the 5s and 1s disconnection times.


     





  • Former Community Member
    0 Former Community Member
    https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=19397&highlight_key=y&keyword1=Disconnection%20lee


    a good old school bonding topic!
  • I do recall that WB now that you have posted it. It was also great to have Mr Blackwell posting on a fairly regular basis. I particularly like Pete LTM’s comment on his brain’s need to declutter to allow new material to enter! Ten years on, I definitely know that feeling!
  • Former Community Member
    0 Former Community Member

    lyledunn:

    I do recall that WB now that you have posted it. It was also great to have Mr Blackwell posting on a fairly regular basis. I particularly like Pete LTM’s comment on his brain’s need to declutter to allow new material to enter! Ten years on, I definitely know that feeling!




    Thanks Lyle, the new forum search facilty is terrible compared with the previous platform :)