but assumes that the relationship between R1 and R2 is equal in terms of resistance. This is not the case in the UK where reduced csa is used for twin and earth cables which, when using the same calculator for prospective fault voltage, would result in higher values and, in consequence, shorter required disconnection times.
OMS:
Or simply use:
Vtouch = Ifault x R2
Where R2 is the resistance of the CPC within the installation, if the installation is bonded - and is the whole resistance of the earth path if not bonded
That should illuminate admirably why bonding in a TT system is a jolly good idea
Regards
OMS
lyledunn:
That's true of course but the OP wanted to know the origin of the 0.4s disconnection time. It probably also explains the 0.2s specified for the TT system. What remains for us to establish the is the origin of the 5s and 1s disconnection times.
lyledunn:
I do recall that WB now that you have posted it. It was also great to have Mr Blackwell posting on a fairly regular basis. I particularly like Pete LTM’s comment on his brain’s need to declutter to allow new material to enter! Ten years on, I definitely know that feeling!