Presumably distribution circuits are allowed to have long disconnect times because they don't expect anyone to actually come into live contact with them very often (apart from the occasional shortly-to-be-deceased sparky fiddling about inside a DB). All the nasty end-user paraphernalia like water heaters, power tools etc are connected further downstream with 0.2/0.4s disconnect times.
AJJewsbury:
I suspect the allowance for 5s disconnection is more to do with the practicalities of achieving discrimination (possibly through several stages of sub-mains) and being able to use a range of overcurrent devices (e.g. fuses) within practical loop impedances, together with the lower likelihood of faults on submains etc - rather than any comprehenive plan for shock protection.
John Peckham:
. . . I do not know if there is any written requirement to lay rubber matting in front of LV panels . . .
Charlie the aged fitter/turner standing on a wet concrete floor whilst operating his lathe grasping a chrome operating handle of his lathe which is supplied from a 40A final circuit? He is wearing his worn out old leather soled army boots.
Playing devil's advocate a little, when Charlie was in training the machine room supply would have been what we now call TNS (or TT), (I'm assuming he is not so old that they had line shafting like this when he started - though perhaps if he started working as an apprentice for UKPN .. ) In such a case the impressed fault voltages and duration are limited, at least if the building wiring has been kept up with modern regs .
A modern building with a TNCS supply should have the steels of the building and any rebar of the concrete floor bonded in any case.
Perhaps he too should have a rubber mat. swarf mat for the modern factory. He should also be provided with modern PPE, including toe protector boots that do not leak.
For what it is worth, I have an island of wooden floor in front of mine for exactly this scenario, but in the manner of the cobbler's barefoot children, and 'do as I say not as I do' , the earthing on my lathe is not quite right anyway, as the centrifugal switch that disconnects the starter winding occasionally arcs out to the case, so the RCD is, ahem, absent.
John Peckham:
Hmm. What about Charlie the aged fitter/turner standing on a wet concrete floor whilst operating his lathe grasping a chrome operating handle of his lathe which is supplied from a 40A final circuit? He is wearing his worn out old leather soled army boots.