This shed, because of its construction should be protected by an independent earth electrode and rccd. The origin, at the fusebox, PME, protects the cable. The DNO req a min distance of 2 metres from the electrode to PME bonded material. The separate earth lead is a good idea in this case for future use, the cpc of the cable being too small to meet the PME regs.
Regards, UKPNWhat P.M.E. regs will not be complied with if just the S.W.A. cable armour is used to supply the building, justifying the need for a separate "earth lead". There will be no main bonding to carry out as the incoming water pipe is plastic?
Zoomup:
UKPN:
This shed, because of its construction should be protected by an independent earth electrode and rccd. The origin, at the fusebox, PME, protects the cable. The DNO req a min distance of 2 metres from the electrode to PME bonded material. The separate earth lead is a good idea in this case for future use, the cpc of the cable being too small to meet the PME regs.