BS 8436 Cable

Hi all I am new to the Forum.


I have a question regarding BS 8436 Compliant Cables. I am aware iof the requirement to protect circuits wired in BS 8436 Cables with "B" Type devices etc due to the requirement to limit fault current in the event of the cable being penetrated by a nail or a screw. However, what if you install the cable clipped direct to the surface and on Cable Tray or basket where the risk of accidental penetration is very low, would it them be acceptable to protect the circuit with "C" Type devices?


I have hunted high and low on the internet for an solution but have failed to find a definitive answer.
Parents
  • Looking at a cable data sheet the answer is no.


    Protective devices used for these cables shall be either Type B to BS EN 60898 or Type B RCBO to BS EN 61009-1. The protective devices shall have a maximum let through energy (l2t) of 42000A2s when used with 1.0mm2 or 1.5mm2 cable and 60000 A2s when used with 2.5mm2 or 4.0mm2 cable.


    It is not designed for use on cable tray, why are you proposing to use it?


    Andy Betteridge
Reply
  • Looking at a cable data sheet the answer is no.


    Protective devices used for these cables shall be either Type B to BS EN 60898 or Type B RCBO to BS EN 61009-1. The protective devices shall have a maximum let through energy (l2t) of 42000A2s when used with 1.0mm2 or 1.5mm2 cable and 60000 A2s when used with 2.5mm2 or 4.0mm2 cable.


    It is not designed for use on cable tray, why are you proposing to use it?


    Andy Betteridge