BS 8436 Cable

Hi all I am new to the Forum.


I have a question regarding BS 8436 Compliant Cables. I am aware iof the requirement to protect circuits wired in BS 8436 Cables with "B" Type devices etc due to the requirement to limit fault current in the event of the cable being penetrated by a nail or a screw. However, what if you install the cable clipped direct to the surface and on Cable Tray or basket where the risk of accidental penetration is very low, would it them be acceptable to protect the circuit with "C" Type devices?


I have hunted high and low on the internet for an solution but have failed to find a definitive answer.
Parents
  • As I have previously stated a number of times, I was simply looking for an alternative to SWA and getting away from an industrial look..


    No big deal. Prysmian have confirmed that BS 8436  identifies B Type breakers only.


    I will will roll with this. Some of the loads are 3 phase some single some loads require C type whilst others will be fine with B Type.


    I would like to thank everybody who has contributed to this post. It has been both interesting and enlightening to read each and every reply. It has indeed been a very positive and rewarding experience.
Reply
  • As I have previously stated a number of times, I was simply looking for an alternative to SWA and getting away from an industrial look..


    No big deal. Prysmian have confirmed that BS 8436  identifies B Type breakers only.


    I will will roll with this. Some of the loads are 3 phase some single some loads require C type whilst others will be fine with B Type.


    I would like to thank everybody who has contributed to this post. It has been both interesting and enlightening to read each and every reply. It has indeed been a very positive and rewarding experience.