AJJewsbury:
OK, if you have a L-N fault, the N counductor at the point of the fault will go up to something like half the normal L-N voltage and hopefully the resulting fault current will cause short-circuit protection will operate. You wouldn't really want to prevent N being pulled up to a higher voltage, as that would prevent the protective device operating as intended.
Or is this a question about SPDs?
Simon Barker:
Assume that the L and N have equal cross-sectional area. Assume that the L and N are approximately equal lengths. Let the resistance of the L up to the fault be (some unknown) value R. From the earlier assumptions, assume that the resistance of N is also R.
By shorting L to N, we're connecting a resistance of 2R across the supply. A current of I = V/2R will flow, where V is the supply voltage. The voltage across the L (from the supply to the short) will be IR = (V/2R)R = V/2. The voltage across the N will also be V/2. So the dead short point will be at V/2 above the supply ground, and V/2 below the supply voltage.