To prevent overvoltage in the neutral conductor, what must be provided in the circuit for protection against overvoltage?

Former Community Member
Former Community Member
To prevent overvoltage in the neutral conductor In the case of a connection between the phase conductor and the neutral conductor, what must be provided in the circuit for protection against overvoltage?
Parents
  • Former Community Member
    0 Former Community Member

    Simon Barker:

    Assume that the L and N have equal cross-sectional area.  Assume that the L and N are approximately equal lengths.  Let the resistance of the L up to the fault be (some unknown) value R.  From the earlier assumptions, assume that the resistance of N is also R.


    By shorting L to N, we're connecting a resistance of 2R across the supply.  A current of I = V/2R will flow, where V is the supply voltage.  The voltage across the L (from the supply to the short) will be IR = (V/2R)R = V/2.  The voltage across the N will also be V/2.  So the dead short point will be at V/2 above the supply ground, and V/2 below the supply voltage.




    Thanks a lot.

Reply
  • Former Community Member
    0 Former Community Member

    Simon Barker:

    Assume that the L and N have equal cross-sectional area.  Assume that the L and N are approximately equal lengths.  Let the resistance of the L up to the fault be (some unknown) value R.  From the earlier assumptions, assume that the resistance of N is also R.


    By shorting L to N, we're connecting a resistance of 2R across the supply.  A current of I = V/2R will flow, where V is the supply voltage.  The voltage across the L (from the supply to the short) will be IR = (V/2R)R = V/2.  The voltage across the N will also be V/2.  So the dead short point will be at V/2 above the supply ground, and V/2 below the supply voltage.




    Thanks a lot.