SW:
Is it acceptable to use TNCS (PME) for supplies to food factories where there are isolated areas deemed Atex (explosive)?
With PME the neutral & earth are linked together before the main ACB and then it is taken in a single cable back to the main star point of the transformer, and then to grounded.
Apparently petrol stations can not be PME. ?
Any thoughts please?
gkenyon:
As mrf says, the neutral and earth must not be combined in the hazardous area.
Also "TN-C-S" isn't always PME.
The risk considered for petrol filling stations is that of diverted Neutral currents from the portions of the system where the neutral and protective conductors are combined, through protective conductors. This is far more likely with a public PME supply than the sort of TN-C-S (transformer to main switcboard link) arrangement you are describing, provided that the distance is short.
So provided the designer of your system is happy that won't happen, as mrf implies, it may well be acceptable.
-2400-:
Most organic powders are explosive.
Flour, sugar and even custard powder have all been responsible for major incidents.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site