I would argue that a fault has already occured by dint of the assembly having insufficient fault rating for the installation.
Err no. The fault has only occurred when you are called out to take a look at the smoking remains and twisted metal hanging off the wall...
It could however certainly be C2 - if the next big fault that comes along that should operate ADS, instead blows the thing to bits.
So single fault to danger, not already dangerous.
Like others I can count on the fingers of one foot the no. of times I have ever seen an MCB fail catastrophically in anything other than film taken during a lab test set up.
The Americans estimate the energy density from arc events using these formulae . I am aware that in the UK we do not normally, but in the US they calculate a rating in joules per cm2 for exposure, and then assume the energy spreads out from the source, to get a safety distance.
However, work beckons, and I'm having "fun" with the formulae in the forum software , so rather than cock it up I will come back and do it properly in another post, probably tonight.
However, even for an open arc, at the risk of spoiling the conclusion, so long as the arc is cut suitably short by a suitable up stream fuse, you do not need much weight in the way of containment until >>10kA at mains voltages (less for an arc partly dissipated in tearing up the case of a breaker.) You could probably make a safe CU out of plastic. ?
I would argue that a fault has already occured by dint of the assembly having insufficient fault rating for the installation.
Err no. The fault has only occurred when you are called out to take a look at the smoking remains and twisted metal hanging off the wall...
It could however certainly be C2 - if the next big fault that comes along that should operate ADS, instead blows the thing to bits.
So single fault to danger, not already dangerous.
Like others I can count on the fingers of one foot the no. of times I have ever seen an MCB fail catastrophically in anything other than film taken during a lab test set up.
The Americans estimate the energy density from arc events using these formulae . I am aware that in the UK we do not normally, but in the US they calculate a rating in joules per cm2 for exposure, and then assume the energy spreads out from the source, to get a safety distance.
However, work beckons, and I'm having "fun" with the formulae in the forum software , so rather than cock it up I will come back and do it properly in another post, probably tonight.
However, even for an open arc, at the risk of spoiling the conclusion, so long as the arc is cut suitably short by a suitable up stream fuse, you do not need much weight in the way of containment until >>10kA at mains voltages (less for an arc partly dissipated in tearing up the case of a breaker.) You could probably make a safe CU out of plastic. ?