Consumer Unit Change Video. Nice.

I liked this video because it is well filmed, has no loud music, and the sparks is very pleasant and explains things well. With plastic conduit I cheat and use manufactured elbows and bends sometimes because they save time and are very consistent and neat. What do you think?




Z.
Parents
  • It would appear the installation was put in to service without main protective bonding see Regulation 641.1. But the bonding was installed the next day so that's alright then?


    How comes the neutral earth problem was not discovered during the dead testing process rather than energising and tripping the RCD? Or is this a version of the 230V bang test?


    Should I mention the absence of a circuit chart, an RCD label, a Mixed colour label and a periodic label or am I being fussy?
Reply
  • It would appear the installation was put in to service without main protective bonding see Regulation 641.1. But the bonding was installed the next day so that's alright then?


    How comes the neutral earth problem was not discovered during the dead testing process rather than energising and tripping the RCD? Or is this a version of the 230V bang test?


    Should I mention the absence of a circuit chart, an RCD label, a Mixed colour label and a periodic label or am I being fussy?