Fuses for showers.

From a electric shower installation manual:


Circuit Protection Table

Circuit Protection Device


Unit Rating (@ 240V)

8.5kW

MCB 40A

Cartridge Fuse 45A


9.5kW

MCB 40/45A

Cartridge Fuse 45A


Why a 45 amp cartridge fuse for a 8.5kW shower or for that matter even the 9.5 kW shower?


I presume it must be time related as the 8.5 kW shower will only load a 40 amp fuse to around 90% of its capacity.


How long can cartridge fuses be run at 90% capacity for?


 Andy B.
Parents

  • Why a 45 amp cartridge fuse for a 8.5kW shower or for that matter even the 9.5 kW shower?


    I presume it must be time related as the 8.5 kW shower will only load a 40 amp fuse to around 90% of its capacity.



    Isn't it just down to 40A not being a preferred size for BS 1361/BS88-3 fuses? - normally your choice would either be 30A (BS 1361)/32A (BS 88-3) or 45A.


      - Andy.
Reply

  • Why a 45 amp cartridge fuse for a 8.5kW shower or for that matter even the 9.5 kW shower?


    I presume it must be time related as the 8.5 kW shower will only load a 40 amp fuse to around 90% of its capacity.



    Isn't it just down to 40A not being a preferred size for BS 1361/BS88-3 fuses? - normally your choice would either be 30A (BS 1361)/32A (BS 88-3) or 45A.


      - Andy.