I guess the thing I'm not getting is, if there was a L-E short at the cooker outlet then the (Sk)² of the 6mm² T&E's E conductor will be sufficient to withstand the I²t of the short circuit current, while if the the short was 2m further away at the far end of the flex 2.5mm² flex, Zs is not significantly higher, so I²t remains the same, while (Sk)² is much reduced and not sufficient. I feel I'm missing something very obvious here.
I guess the thing I'm not getting is, if there was a L-E short at the cooker outlet then the (Sk)² of the 6mm² T&E's E conductor will be sufficient to withstand the I²t of the short circuit current, while if the the short was 2m further away at the far end of the flex 2.5mm² flex, Zs is not significantly higher, so I²t remains the same, while (Sk)² is much reduced and not sufficient. I feel I'm missing something very obvious here.