The existing cooker circuit is 6mm² on a B40. The customer wants to replace the free-standing cooker with 2 built-in ovens and an induction hob. Will each cable from cooker outlet to device need to be the full 6mm², (e.g HO7RN-F) or can I get away with anything smaller and more convenient (e.g. what's supplied with each oven/hob, if anything)? The final purchasing choice hasn't been made yet, so I don't know whether any of the devices will be suitable for a 13A plug/FCU, which can obviously accept a smaller cable.
What is the difference in resistance between the 6mm and 2.5mm for your tail to the cooker? If you really are that close to the mcb not tripping, I suggest you have far more wrong with the circuit.
What is the difference in resistance between the 6mm and 2.5mm for your tail to the cooker? If you really are that close to the mcb not tripping, I suggest you have far more wrong with the circuit.