mapj1:
TT earth islanding for the building or the rooms involved is the nearest you will get to that.
You can do it but you need to have an RCD up front, perhaps 100mA slow acting, and then from then onwards you then ignore the company earth, and use the local electrode. The two earth zones must not meet, so plastic radiator pipes or boxing in if parts of the building are to one earthing system and the rest to another.
The two earth zones may require separation by the DNO. It may not be achievable in a built up area, and might depend on the extent of the PME and arrangement of the distribution and other metallic services in the area.
DNOs aren't always keen on two different earthing arrangements within a building either.
An earthing approach to BS EN 50310 would, I believe, be far superior in most cases, and a TN system earthing arrangement is usually better.
To add any value at all in terms of noise ingress you need to have some mains filtering on the circuits or perhaps just before the whole CU feeding the quiet zone.
We tend to specify things like these on RF chambers, where we mount them on / stuck through the chamber wall, with the dirty side out, clean side inwards for receiver tests, and the other way round for transmitter or pulse power testing, but that may be overkill and you probably need to keep an eye on the earth leakage the filters cause.
What scares me somewhat is the fact that the so called 'Specialist' is also suggesting that an entirely separate Earth be installed, with no bonding to the incomer, and that when recording, the technician can switch over to this supposed clean earth and not utilise the incomer. If I am correct, this is not common practice in the UK and not something that is acceptable!
mapj1:
Transformer isolation will be good for low frequency junk, less useful for higher frequencies, RF tends to also be a problem for audio as well as direct in -band break though, as it intermodulates to create audible responses.
However any isolation will only be as good as the separation of pre- and post filtered wiring in any case, running them alongside for any length will largely undo the good. Hence shielded walls where it really matters, which is not here.
If we are looking at how the electrical system deals with harmonics and reception of radiated emissions, a centre-tapped transformer (earth the centre-tap) is much better for single-phase supplies.
I'm not aware of any restriction requiring you to use the DNOs earth after the meter, you can TT one house in a row, or indeed one room in a building, much as you would a garden shed.
However, if there are shared services these do need some thought, and so does where the TT earth electrode goes needs to be far away from sources of current injection or removal from the terra firma, I suspect we are saying the same thing in different words.