mapj1:
Transformer isolation will be good for low frequency junk, less useful for higher frequencies, RF tends to also be a problem for audio as well as direct in -band break though, as it intermodulates to create audible responses.
However any isolation will only be as good as the separation of pre- and post filtered wiring in any case, running them alongside for any length will largely undo the good. Hence shielded walls where it really matters, which is not here.
If we are looking at how the electrical system deals with harmonics and reception of radiated emissions, a centre-tapped transformer (earth the centre-tap) is much better for single-phase supplies.
I'm not aware of any restriction requiring you to use the DNOs earth after the meter, you can TT one house in a row, or indeed one room in a building, much as you would a garden shed.
However, if there are shared services these do need some thought, and so does where the TT earth electrode goes needs to be far away from sources of current injection or removal from the terra firma, I suspect we are saying the same thing in different words.
mapj1:
Transformer isolation will be good for low frequency junk, less useful for higher frequencies, RF tends to also be a problem for audio as well as direct in -band break though, as it intermodulates to create audible responses.
However any isolation will only be as good as the separation of pre- and post filtered wiring in any case, running them alongside for any length will largely undo the good. Hence shielded walls where it really matters, which is not here.
If we are looking at how the electrical system deals with harmonics and reception of radiated emissions, a centre-tapped transformer (earth the centre-tap) is much better for single-phase supplies.
I'm not aware of any restriction requiring you to use the DNOs earth after the meter, you can TT one house in a row, or indeed one room in a building, much as you would a garden shed.
However, if there are shared services these do need some thought, and so does where the TT earth electrode goes needs to be far away from sources of current injection or removal from the terra firma, I suspect we are saying the same thing in different words.