4000 Watts divided by 240 volts = 16.7 amps, if you divide be 230 it comes out at 17 .4 amps.
It doesn't work like that.
If you are going to use 230V for design then it will be 16A - surprise.
At 250V, it will be 17.4A so perhaps one should allow for that just in case.
If you look at a selection of double ovens you will find the manufacturers rating stated as required for the fuse or MCB doesn’t tally with the actual ratings they give for the ovens.
Sparkingchip:
As I suspected the manufacturer has overstated the circuit requirement.
That oven will be quite safe on a 2.5 mm circuit with a 20 amp MCB or RCBO. That doesn’t particularly help if you don’t have such a circuit.
It is almost on the point of being able to be connected to a socket ring circuit with a 16 amp MCB at the point it is connected to that circuit.
4000 Watts divided by 240 volts = 16.7 amps, if you divide be 230 it comes out at 17 .4 amps.
If you look at a selection of double ovens you will find the manufacturers rating stated as required for the fuse or MCB doesn’t tally with the actual ratings they give for the ovens.
To be perfectly honest in my home I would prefer to see it connected to a socket ring circuit using a 16 amp MCB than connected to the shower circuit, after all the existing oven has been wired that way for many years.
Though I would still recommend a new circuit is installed.
Sparkingchip:
Is the existing oven gas or electric?
Is the existing oven supplied by a plug from socket circuit or goes it have its own circuit, if it foes have its own circuit what size is the cable and the protective device got it in the consumer unit?
Exactly what oven have you bought?
Andy Betteridge
But that is kind of the point, is it not?
Is that a deflection or a cloud (sic)?
Again, what diversity can you apply to a shower?
Regards
BOD
Chris Pearson:
Thank you for the photograph. I feel obliged to make a couple of observations (with all due respect):
(1) It is not a large property, so a shower for emergency use seems a little lacking in credibility;
(2) There isn't a lot of room for a double oven. I also note what appears to be a stack of at least three microwaves. ?
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.