Sparkingchip:
As I suspected the manufacturer has overstated the circuit requirement.
That oven will be quite safe on a 2.5 mm circuit with a 20 amp MCB or RCBO. That doesn’t particularly help if you don’t have such a circuit.
It is almost on the point of being able to be connected to a socket ring circuit with a 16 amp MCB at the point it is connected to that circuit.
4000 Watts divided by 240 volts = 16.7 amps, if you divide be 230 it comes out at 17 .4 amps.
If you look at a selection of double ovens you will find the manufacturers rating stated as required for the fuse or MCB doesn’t tally with the actual ratings they give for the ovens.
To be perfectly honest in my home I would prefer to see it connected to a socket ring circuit using a 16 amp MCB than connected to the shower circuit, after all the existing oven has been wired that way for many years.
Though I would still recommend a new circuit is installed.
4000 Watts divided by 240 volts = 16.7 amps, if you divide be 230 it comes out at 17 .4 amps.
It doesn't work like that.
If you are going to use 230V for design then it will be 16A - surprise.
At 250V, it will be 17.4A so perhaps one should allow for that just in case.
If you look at a selection of double ovens you will find the manufacturers rating stated as required for the fuse or MCB doesn’t tally with the actual ratings they give for the ovens.
cfcman:
Chris Pearson:
Thank you for the photograph. I feel obliged to make a couple of observations (with all due respect):
(1) It is not a large property, so a shower for emergency use seems a little lacking in credibility;
(2) There isn't a lot of room for a double oven. I also note what appears to be a stack of at least three microwaves. ?Oh dear it seems that a picture is not always worth a thousand words :0(
I'm not entirely sure how your inferences were derived regarding the size of the property, or the "credibility" of a shower for emergency use - I'm not entirely sure what was meant by that?....
But to clarify:
- The property is a 3-storey townhouse. I'm not sure what your definition of "large" is, but my guess is that the average UK homeowner would not describe it as "small"
- The photo shows a small corner of a reasonably-sized kitchen (approximately 12 square metres)
- There is plenty of space for a double oven to replace the existing single oven (I don't see much value in another photo to illustrate this particular point)
- The property has three bathrooms - one on each floor. The photo shows the kitchen on the middle floor. The adjoining bathroom is used as a WC, but also has the electric shower in question, which was installed 10 years ago, specifically as a backup in the event of a boiler failure. The associated power supply was installed at the same time.
- Those are indeed three microwave ovens - well spotted.
I'm not entirely sure how/whether any of this is relevant, but I guess more information is usually better than less....