Derating Conductors due to bundling inside Low voltage switchgear

Former Community Member
Former Community Member
I know when it comes to conductors inside switchgear the regulations for  IEC-61439 Annex H pages 111 and 112 apply.

If cables installed in free air outside the enclosure regs of BS 7671 Appendix 4 Section 7 and IEC-60364-5-52 would apply.

If we have many cables installed in free air (let's say 15) and they are distant from each others by more than 2 cable diameter (hence no derating factor for bunching shall apply) but they would be bundled for a distance(L) inside enclosure before they directly terminate in C.B's what would be the case here?

Shall we use the rating for the whole run of cables obtained by IEC-61439 and apply high derating factors or it depends on the length of (L) of the bundling? 

Knowing that in case of thermal insulation of conductor BS 7671 Reg. 523.9 takes in consideration the Length of the part of conductor that is thermally insulated.
Parents
  • Former Community Member
    0 Former Community Member
    I suspect the 'usual practice' in the UK is not to specifically calculate for inside the DB - just work with the ratings for the rest of the circuit - but at the same time lacing/bunching/cable-tying conductors together inside a DB is considered poor practice." In many case bundling is not evitable but also I think in lighting panel boards where there are many branch circuits let's say 54 way enclosure, the conductors are feeding lighting and sockets outlets where the diversity factor is very low and hence it's rare that a problem shall occur due to bundling.On the other hand where the panel board is feeding sub feeder panel and diversity factor is relatively high, the enclosure is big in comparison with outgoing feeders and generally no tied bundling is needed.

    But as inspector and you would work by the book I think it would be a problem and hence derating factor along the whole circuit run shall follow IEC 61439-1.

    I think in France it is a good practice to terminate home runs by terminal blocks inside the enclosure, here the panel builder is responsible for his panel board conductors and installation contractor is responsible for the external conductors. and hence if some derating shall occur is for the short length inside enclosure(between terminal and C.B).

    On the other hand, there is something interesting in NEC is that they allow (with 40 percent max. fill factor in wire space) for 60cm bundling with no derating or (10 percent of whole run or 3 meters whichever is lesser), noting that BS standard lighting panel boards are very similar to UL-listed panel boards and termination occurs directly on CB but using above stated exemptions will relieve contractor from derating conductors due to bundling for short length. I was searching for similar exemptions in BS 7671 standard but I couldn't find.I think sooner or later we shall see such exemptions in BS 7671.
Reply
  • Former Community Member
    0 Former Community Member
    I suspect the 'usual practice' in the UK is not to specifically calculate for inside the DB - just work with the ratings for the rest of the circuit - but at the same time lacing/bunching/cable-tying conductors together inside a DB is considered poor practice." In many case bundling is not evitable but also I think in lighting panel boards where there are many branch circuits let's say 54 way enclosure, the conductors are feeding lighting and sockets outlets where the diversity factor is very low and hence it's rare that a problem shall occur due to bundling.On the other hand where the panel board is feeding sub feeder panel and diversity factor is relatively high, the enclosure is big in comparison with outgoing feeders and generally no tied bundling is needed.

    But as inspector and you would work by the book I think it would be a problem and hence derating factor along the whole circuit run shall follow IEC 61439-1.

    I think in France it is a good practice to terminate home runs by terminal blocks inside the enclosure, here the panel builder is responsible for his panel board conductors and installation contractor is responsible for the external conductors. and hence if some derating shall occur is for the short length inside enclosure(between terminal and C.B).

    On the other hand, there is something interesting in NEC is that they allow (with 40 percent max. fill factor in wire space) for 60cm bundling with no derating or (10 percent of whole run or 3 meters whichever is lesser), noting that BS standard lighting panel boards are very similar to UL-listed panel boards and termination occurs directly on CB but using above stated exemptions will relieve contractor from derating conductors due to bundling for short length. I was searching for similar exemptions in BS 7671 standard but I couldn't find.I think sooner or later we shall see such exemptions in BS 7671.