I know when it comes to conductors inside switchgear the regulations for IEC-61439 Annex H pages 111 and 112 apply.
If cables installed in free air outside the enclosure regs of BS 7671 Appendix 4 Section 7 and IEC-60364-5-52 would apply.
If we have many cables installed in free air (let's say 15) and they are distant from each others by more than 2 cable diameter (hence no derating factor for bunching shall apply) but they would be bundled for a distance(L) inside enclosure before they directly terminate in C.B's what would be the case here?
Shall we use the rating for the whole run of cables obtained by IEC-61439 and apply high derating factors or it depends on the length of (L) of the bundling?
Knowing that in case of thermal insulation of conductor BS 7671 Reg. 523.9 takes in consideration the Length of the part of conductor that is thermally insulated.