TPN SOCKETS OUTDOORS

If this installation was new, would you provide 30mA RCD protection?


 7cd39c353faf63f8858d579f4fa7d8bf-huge-f6a6e2f8-50d3-4f39-bedf-22409da3aab1.jpg
Parents
  • Since it would be classed as 'Portable Equipment Used Outdoors' then depending upon motor rating, all of the conveyors we inspect/test/connect up have to have 30ma rcd protection. Generally, this is via a plug/socket arrangement with an integral 4 pole RCD , with the socket being fed from a main control panel and it's wiring protected accordingly for the rating.
Reply
  • Since it would be classed as 'Portable Equipment Used Outdoors' then depending upon motor rating, all of the conveyors we inspect/test/connect up have to have 30ma rcd protection. Generally, this is via a plug/socket arrangement with an integral 4 pole RCD , with the socket being fed from a main control panel and it's wiring protected accordingly for the rating.