TPN SOCKETS OUTDOORS

If this installation was new, would you provide 30mA RCD protection?


 7cd39c353faf63f8858d579f4fa7d8bf-huge-f6a6e2f8-50d3-4f39-bedf-22409da3aab1.jpg
Parents

  • mapj1:


    The bigger source of grief in terms of earth leakage will be if there is a VFD in the box




    Although not often done because of cost, it's a general recommendation to install isolating transformers at the input to variable speed drives to localise the protective conductor currents ...

Reply

  • mapj1:


    The bigger source of grief in terms of earth leakage will be if there is a VFD in the box




    Although not often done because of cost, it's a general recommendation to install isolating transformers at the input to variable speed drives to localise the protective conductor currents ...