The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
broadgage:
As an extreme but illustrative example consider a circuit wired in 2.5mm SWA without any de-rating for grouping etc, and protected by a 20 amp fuse. If the cable was long enough, the fuse might never operate on a phase to neutral short circuit. But would the cable be damaged? I suspect not.
In most real world cases voltage drop would be a problem first.
broadgage:
As an extreme but illustrative example consider a circuit wired in 2.5mm SWA without any de-rating for grouping etc, and protected by a 20 amp fuse. If the cable was long enough, the fuse might never operate on a phase to neutral short circuit. But would the cable be damaged? I suspect not.
In most real world cases voltage drop would be a problem first.
We're making some changes behind the scenes to deliver a better experience for our members and customers. Posting and interactions are paused. Thank you for your patience and see you soon!
For more information, please read this announcement