Sparkymania:
Thanks Farmboy
I have listened to that one.
Talks about taking PSCC at the end of circuit but doesn't go into why you can't just use the line-neutral loop impedance and compare it to the max Zs as I would have thought that would be the same. Same fault current to trip MCB whether to earth or neutral.
Sparkymania:
If the L-N loop imp. is too high won't that mean the current flow will then be too low, the same as it would be for L-E loop imp.
Not necessarily - there is no fixed disconnection time for an L-N fault in a TN-C-S, TN-S or TT system. The requirement is to disconnect before the cable is damaged. So, the requirement is NOT the loop impedance, but the Adiabatic Criterion (or, for disconnection times longer than 5 s, calculated in accordance with BS 7454) - see Regulation 434.5.2.
We don't test for PEFC to make sure an MCB will trip on an earth fault.
That's because we need disconnection time in accordance with Chapter 41 - and therefore we check loop impedance in accordance with the relevant Table 41.2 to 41.5 (adjusted by the "rule of thumb" of course, as we are taking measurements at 20 deg C, not the operating temperature of the cable 70 deg C).
Why use loop imp for earth fault but PSCC for short circuit? Aren't we doing the same thing for both faults?
The prospective fault current at the start of the circuit is greater than the prospective fault current at the end of the circuit, and hence this is really the reason we don't often do pfc checks at the end of the circuit, because usually the thing we are worried about for damage to the cable is worse at the DB.
By taking Zs and comparing it to max Zs for the OCPD we are making sure there will be enough fault current.
We would already know the max Zs so why not just take a second tests after Zs at the point of test Z l-n?
You could to that, but then you'd have to work out what the current is to make use of the adiabatic criterion, or BS 7454, so it's easier to measure the current.
It wouldn't matter if the circuit had a reduced CPC size as you would be taking both readings. It's also dependent on the PEFC and PSCC at the origin to begin with so taking both impedance readings will give you the info that is needed.
Not necessarily. But I agree it's not really necessary to take the measurement if the cable is sized correctly in accordance with BS 7671 - the problem for L-N and L-L faults as I said happens further up the cable, not further down.
Volt drop is usually a limiting factor if you do the calculations, and have selected the cable in accordance with BS 7671.
Farmboy. FYI for some reason your second post did not come up here. The only reason I know you posted again was the email I got.
davezawadi:
There is an important point to remember here and that is that Zs is calculated on non RCD circuits to give a disconnection time of 0.4 seconds, and it takes quite a bit more resistance to take this number up to 5 seconds, which is about when you should start to think there may be a short circuit problem.
Not with mcb's, because of the threshold between thermal and magnetic operation. Having said that, in general an mcb will perform better than the worst-case curves shown in BS 7671.