broadgage:
As an extreme but illustrative example consider a circuit wired in 2.5mm SWA without any de-rating for grouping etc, and protected by a 20 amp fuse. If the cable was long enough, the fuse might never operate on a phase to neutral short circuit. But would the cable be damaged? I suspect not.
In most real world cases voltage drop would be a problem first.
According to the book the time-current table for a 60898 B, C or D 32 would allow a continuous current of 46A and not trip.
I'm wondering how the cable would cope with that.