My question was enquiring about different methods but also if an earth was required along with the live and switched live for eddy current reasons
Baldyhugh:
Thanks Z
I don’t think that my reading of 542.4.1 says that an earth terminal must be provided at a plastic accessory incase future alterations require an earth terminal, for example, changing a plastic light switch to a metal.
So in my example of plastic conduit and plastic switch and box coming from a steel trunking, it is actually a two gang switch on two different circuits, it is acceptable to have (in this example) just a live and switch live for each circuit down to the switch but an earth isn’t required as regards eddy current considerations as there can be no possibility of an earth fault at the switch due to its plastic construction?
Please see 411.3.1.1
AJJewsbury:
So in my example of plastic conduit and plastic switch and box coming from a steel trunking, it is actually a two gang switch on two different circuits, it is acceptable to have (in this example) just a live and switch live for each circuit down to the switch but an earth isn’t required as regards eddy current considerations as there can be no possibility of an earth fault at the switch due to its plastic construction?
That's about the size of it!
Please see 411.3.1.1
I'd suggest otherwise.
If it's an all-insulated switch then protection against electric shock is by double or reinforced insulation rather than ADS (how could ADS operate without any earthed metalwork?) Thus it's not section 411 that applies but 412. It's therefore the (not greatly dissimilar) regulation 412.2.3.2 we should be looking at. 412.2.3.2 does have a get-out though (via 412.1.2) where the system is controlled so that unauthorised changes (such as the introduction of class I accessories) can't be made.
- Andy.
my example involves a two gang switch on two different circuits so there will be a two lines from the db, one to each switch and two switch lines, one leaving each switch. What are your views on a single conduit containing different circuits?