Whilst these arrangements are absolutely OK for a switched alternative to the normal supply, and illustrate very well the situation about leaving the distributor's means of earthing connected, I feel it's only fair to readers to point out that they won't support either self-use or export of stored energy in connected mode. Therefore, switching for island mode in a prosumers' electrical installation is a little more tricky, involving switching of an N-E bond. This is because you can't have two N-E bonds at the same time ... and BS 7671 doesn't permit you to rely on the supplier's N-E bond even in PME.
Whilst these arrangements are absolutely OK for a switched alternative to the normal supply, and illustrate very well the situation about leaving the distributor's means of earthing connected, I feel it's only fair to readers to point out that they won't support either self-use or export of stored energy in connected mode. Therefore, switching for island mode in a prosumers' electrical installation is a little more tricky, involving switching of an N-E bond. This is because you can't have two N-E bonds at the same time ... and BS 7671 doesn't permit you to rely on the supplier's N-E bond even in PME.