Zs measurement on an Off Peak supply.

On an EIC for just metal board changes, one on "On Peak" and one on "Off Peak", what is the current thinking regarding entering Zs for the latter? - using an estimate of (R1 + R2) + Ze or just enter a Limitation, since this is an existing installation ?   


Jaymack
Parents
  • Aren't your test leads long enough to reach from one board to the other and/or from the DNO earth terminal to the off-peak earth bar?


    Andy B.
Reply
  • Aren't your test leads long enough to reach from one board to the other and/or from the DNO earth terminal to the off-peak earth bar?


    Andy B.