On an EIC for just metal board changes, one on "On Peak" and one on "Off Peak", what is the current thinking regarding entering Zs for the latter? - using an estimate of (R1 + R2) + Ze or just enter a Limitation, since this is an existing installation ?   


Jaymack
  • Sleeping bag and a flask required

  • Blencathra:

    Sleeping bag and a flask required




    Is a measurement of Ze (or Zs) actually required by BS 7671?


     

  • Is there a 24 hour supply from the same origin - if so this can be used to verify the earthing and supply is OK, and get a Zs for the external part. I;d be tempted to do the rest by calculation or dead tests and add it on.
  • Aren't your test leads long enough to reach from one board to the other and/or from the DNO earth terminal to the off-peak earth bar?


    Andy B.

  • gkenyon:




    Blencathra:

    Sleeping bag and a flask required




    Is a measurement of Ze (or Zs) actually required by BS 7671?


     


     




    Enquiry

  • Sometimes there's a boost button on the e7 meter
  • Adequate live testing from the normal supply and sufficient dead testing to the off peak supply to give the most reasonable conclusion possible.