This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Zs measurement on an Off Peak supply.

On an EIC for just metal board changes, one on "On Peak" and one on "Off Peak", what is the current thinking regarding entering Zs for the latter? - using an estimate of (R1 + R2) + Ze or just enter a Limitation, since this is an existing installation ?   


Jaymack
Parents Reply Children
No Data