TT Supply and SPDs for EV Charging point
Got a job to do when the lock down ends.
Customer is having a EV Charging point installed by a 3rd party into his garage, and the consumer unit in the garage needs upgrading (extra way) with a Type A RCD (EVCE has DC monitoring internally) .  Existing supply to garage is 16A and due to the house being rented customer doesn't want to replace the buried cable, so EV Charging Installer is going to de-rate the charger to 3kW.
Existing installation is TT, supplied by overheads and CRL would recommend SPDs are fitted.  Garage is fed from a dual RCD board with Type AC RCDs.
So 1st of all I have to take the garge supply out of the existing consumer unit and protected it was a Type A 100mA time delayed RCD with a relevant MCB (20A).
Now because the supply is overhead I'm led to believe that a Type 1 SPD is required to be fitted at the origin.  One supplier of a Type 1 SPD, recommends that it is protected by a 63A MCB, and also says an RCD should not be installed upstream of this type of SPD as there is potential leakage.  534.4.7 also confirms this.
So I now have to put the following components in a new enclosure (or enclosures), 63A MCB, SPD, RCD and 20A MCB, in that order.  Because its a domestic then these should all be enclosed in a metal enclosure, I assume these come under the 'Switchgear assemblies' definition.  But I am nervous that I would have incoming tails to a metal enclosure that connect to a MCB which then connects to the SPD before we get to RCD protection!
How do I overcome this and keep to the regs?
  • If the garage is not connected directly to the domestic premise, plastic enclosures can be used.
    Also you could use plastic enclosures and cover with a metal box.
  • But the SPD/RCD etc has to be in the house near the meter!
  • I might be mistaken but I don't think a type 1 is required unless there's a lightning protection system installed.
    I might be tempted by a SPD that doesn't need an upstream MCB and in a plastic enclosure - e.g. something like https://www.tlc-direct.co.uk/Products/WYREC2SPD.html
    (fortunately such an assembly doesn't meet BS 7671's definition of switchgear or a consumer unit).
    As long as they're connected as connection type 2 (CT2) - i.e. the SPD element for L connects to N rather than PE - they can go upstream of RCDs on a TT system.
  • Yep - the main point of a type 1 SPD is to bond the electrical system to the lighting protection system so that in a direct lighting strike, cables, water pipes etc are all at a similar potential and flash-over doesn't occur (which might start a fire). There is no guarantee that such an SPD is also suitable for protecting your electrical system from transients; that's what a type 2 is for.
  • The SPD I'm looking at is a Type 1/2.
    BS7671 doesn't specifically specify Type 1 for overhead supply cables but talking to a SPD specialist they suggest its mentioned in BS EN 62305.  Also an online SPD selector (different company to other info source) comes up with the same result - Type 1/2 required because of overhead lines.
  • BEAMA recommends a type 1 be installed when the installation has a LPS installed and/or is supplied by o/head lines and/or the building has a metal roof:
    https://www.beama.org.uk/resourceLibrary/beama-surge-protection-guide-.html
    F