TT Supply and SPDs for EV Charging point

Got a job to do when the lock down ends.

Customer is having a EV Charging point installed by a 3rd party into his garage, and the consumer unit in the garage needs upgrading (extra way) with a Type A RCD (EVCE has DC monitoring internally) .  Existing supply to garage is 16A and due to the house being rented customer doesn't want to replace the buried cable, so EV Charging Installer is going to de-rate the charger to 3kW.

Existing installation is TT, supplied by overheads and CRL would recommend SPDs are fitted.  Garage is fed from a dual RCD board with Type AC RCDs.

So 1st of all I have to take the garge supply out of the existing consumer unit and protected it was a Type A 100mA time delayed RCD with a relevant MCB (20A).

Now because the supply is overhead I'm led to believe that a Type 1 SPD is required to be fitted at the origin.  One supplier of a Type 1 SPD, recommends that it is protected by a 63A MCB, and also says an RCD should not be installed upstream of this type of SPD as there is potential leakage.  534.4.7 also confirms this.

So I now have to put the following components in a new enclosure (or enclosures), 63A MCB, SPD, RCD and 20A MCB, in that order.  Because its a domestic then these should all be enclosed in a metal enclosure, I assume these come under the 'Switchgear assemblies' definition.  But I am nervous that I would have incoming tails to a metal enclosure that connect to a MCB which then connects to the SPD before we get to RCD protection!

How do I overcome this and keep to the regs?
Parents
  • The SPD I'm looking at is a Type 1/2.

    BS7671 doesn't specifically specify Type 1 for overhead supply cables but talking to a SPD specialist they suggest its mentioned in BS EN 62305.  Also an online SPD selector (different company to other info source) comes up with the same result - Type 1/2 required because of overhead lines.
Reply
  • The SPD I'm looking at is a Type 1/2.

    BS7671 doesn't specifically specify Type 1 for overhead supply cables but talking to a SPD specialist they suggest its mentioned in BS EN 62305.  Also an online SPD selector (different company to other info source) comes up with the same result - Type 1/2 required because of overhead lines.